Post a question or comment
Credit Filters
Indoor Chemical and Pollutant Source Control
Filter by location
Forum
Topic
Replies
Recent

Convenience printers/copiers

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  Mike D  on 

How do we show that the printers/copiers to be installed are just convenience ones and therefore will not require separate exhaust?

3
Director - Green Building Advisory
Colliers International Ltd.
LEEDuser Basic Member
201 thumbs up
Wed Aug 23, 2023, 3:31 pm

Entryway systems

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  K Pomperada  on 

Our project is an office building already being occupied by tenants, and the entryway system measures only 9 ft. lacking 1ft from the requirement by LEED.

0

entryway walk-off system in front of each retail shop in CS?

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  Alicja Bieszyńska  on 

Our project is a mixed use building where groundfloor constitutes retail services and floors from one up are for tenants. Taking into account that this is a CS certification, do we need to install

2
Founder & Community Director
Metricorps
LEEDuser Expert
7781 thumbs up
Fri Jun 14, 2019, 7:59 pm

Is painted gypsum considered a hard-lid ceiling

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  Edgar Arevalo  on 

I am looking at the "Negatively Pressurized Rooms" section for this credit, and I noticed that separation method includes an option for hard-lid ceiling.  I am curious, after looking at the fi

0

Roll-out mats details

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  Summer   on 

Anyone can confirm if all roll-out mats should be provided with zocallo to insert the carpet?

1
Fri Nov 9, 2018, 3:41 pm

Entryway system

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  Elodie DUMAS  on 

Our project is an office building where groundfloor is componed by retails and services dedicated to unknown tenants. Taking into account that this is a CS certification, do we need to install ent

4
Senior Sustainability Manager
WSP
LEEDuser Expert
53 thumbs up
Tue Aug 7, 2018, 1:48 pm

MERV 13 Filtration

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  Donald Green  on 

In a CS project that is a renovation with existing mechanical equipment - does the existing mechanical equipment need to have the MERV 13 filtration?

1
Fri Nov 10, 2017, 10:34 pm

Entryways system disntance 10ft

CS-2009 IEQc5:Indoor Chemical and Pollutant Source Control
posted by  gabriel Morales  on 

Hello, architecture according to our main lobby, meeting with the distance of 10ft mat we complicated for users coming from the parking lots. The design team has proposed installing a section of

1
Fri Jul 13, 2012, 5:34 pm