Post a question or comment
Credit Filters
Outdoor Air Delivery Monitoring
Filter by location
Forum
Topic
Replies
Recent

Alternative to OA airflow measurement device at Building AHU

CI-2009 IEQc1:Outdoor Air Delivery Monitoring
posted by  Kristopher Baker   on 

So like many on this thread, i have a LEED CI project that is 1/3 of 1 floor and is served by the base building AHU that is outside the scope and LEED boundary of the project.

1
Tue Sep 8, 2015, 3:36 pm
1
Tue Dec 28, 2010, 11:12 pm

Locker rooms

CI-2009 IEQc1:Outdoor Air Delivery Monitoring
posted by  Agnieszka Rylska  on 

Are CO2 sensors required in locker rooms? Loker rooms are non-regularly occupied spaces but they are also densely-occupied spaces.

1
Sat Aug 26, 2017, 10:50 pm

CO2 in small space / private offices

CI-2009 IEQc1:Outdoor Air Delivery Monitoring
posted by  CT G  on 

Dear all, Once I saw a LEED Interpretation stating that small spaces, or private offices, could be exempt of installing CO2 sensors to comply with this credit, for CI only, not to NC. I can't find

3
Default Avatar
LEEDuser Premium Member
19 thumbs up
Fri Feb 19, 2016, 9:35 pm

100% OA VAV Base Building system

CI-2009 IEQc1:Outdoor Air Delivery Monitoring
posted by  Christie Rimes  on 

Hi, the CI project I am working on uses only the base building system supply for meeting rooms with between 2 and 8 people.

2
Principal, Energy and Engineering Leader
DLR Group | Westlake Reed Leskosky
LEEDuser Expert
267 thumbs up
Sun Jan 10, 2016, 10:08 pm

Non Regularly Occupied Spaces

CI-2009 IEQc1:Outdoor Air Delivery Monitoring
posted by  James Keohane  on 

RE: CO2 Sensors for Densely Occupied Spaces Are spaces designated as Non-regularly Occupied Spaces excluded from consideration as Densely Occupied Spaces??

3
Thu Sep 10, 2015, 2:21 am

Multiple AHU from shared OA

CI-2009 IEQc1:Outdoor Air Delivery Monitoring
posted by  Wayne Mason  on 

I have a situation where a mechanical room (4 actually) has two SCU units and one OA inlet.

2
Mechanical Engineer
Integral Group
LEEDuser Expert
342 thumbs up
Tue Sep 4, 2012, 4:31 pm

IEQc1 Language

CI-2009 IEQc1:Outdoor Air Delivery Monitoring
posted by  John Kitsalis  on 

Hello, I understand the part of the credit involving CO2 sensors but do not understand the language involving the outdoor airflow measurement device: "Complete Table IEQc1-2 for all mechanical ve

3
Default Avatar
Principal
New England Engineering, Inc.
LEEDuser Basic Member
2 thumbs up
Wed Aug 22, 2012, 9:30 pm