IEQp1: Minimum Indoor Air Quality Performance

CI-2009 IEQp1:Minimum IAQ Performance
posted by  Arslan Faisal  on 

We are working on a plaza which have office spaces. we submit this project. But in the review report they asking the following documents.

0

IEQp1 Compliance ?

CI-2009 IEQp1:Minimum IAQ Performance
posted by  George Bender  on 

Office floor of a high rise building trying to obtain LEED sliver. Floor is served by AHU, which serves 30 other floors not in scope. VAV's serve multiple zones on this floor.

0

IEQp1 Design Review told me I have multizone not single

CI-2009 IEQp1:Minimum IAQ Performance
posted by  Kasandra Martin  on 

I have roof top units. Each serves several rooms. One system serves a single room with single thermostat.

0

Transfer Air for IEQp1 achievement

CI-2009 IEQp1:Minimum IAQ Performance
posted by  Ricardo Sá  on 

Hello, I'm currently working on a project of a huge supermarket. The building has warehouses and storage rooms.

0
1
Wed Dec 29, 2010, 1:33 pm

RE:62MZ calc. spreadsheet Vdzd & Ds inputs

CI-2009 IEQp1:Minimum IAQ Performance
posted by  Bobby Ghataura  on 

In the 62MZ calc, i created zones that have heating and potentially critically zones, but im having an issue with the results; for Vdzd, i enter the airflow rate that corresponds to the minimum VAV

1
Fri Dec 21, 2012, 7:04 pm

Multi-zone system when single AHU supplying OA to FCUs?

CI-2009 IEQp1:Minimum IAQ Performance
posted by  Poorva Keskar  on 

We have 2 AHUs supplying OA to individual FCUs via a separate duct as per ASHRAE 62 intake requirement. The mixing occurs at the individual FCUs and then supplied to the zone.

1
Thu Nov 14, 2013, 1:49 pm

IEQp1 using indoor packaged DX units

CI-2009 IEQp1:Minimum IAQ Performance
posted by  Edgar Arevalo  on 

I'm in a bit of a funk. I have a office space that populates two floors of a building.

1
Wed Dec 24, 2014, 3:20 pm

IAQ Procedure is NOT acceptable?

CI-2009 IEQp1:Minimum IAQ Performance
posted by  James Keohane  on 

I recently received a Design Review comment advising that the IAQ procedure included in Chapter 6 of the ASHRAE 62.1-2007 is not an acceptable tool to demonstrate compliance.

1
Tue Jan 24, 2017, 2:21 pm

outdoor air rate for kitchens

CI-2009 IEQp1:Minimum IAQ Performance
posted by  Adam Targowski  on 

I would like to ask if there's any requirement regarding outdoor air suplly to a kitchen located in an office area? In ASHRAE 62.1-2007 Table 6-1 a kitchen is not mentioned.

1
Fri Dec 21, 2012, 7:57 pm