CO2 sensors in retail spaces
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Agnieszka Rylska on
Should retail spaces in a shopping mall have CO2 sensors? Does anyone know if shops are treated as densely occupied spaces?
How many CO2 sensors are required per space?
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by William Wong on
Credit requires to monitor CO2 level for densely occupied spaces. Is there any requirements for the minimum no. of sensors per space / sq ft?
LEED Core and Shell 2009 (V 3) for IEQ c1, IEQ c5 and IEQ 6
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Himanshu Dehra on
We wish to attempt and submit documentation {LEED Core and Shell 2009 (V 3)} for following credits (with no control on Tenant Spaces): 1. Outdoor Air Delivery Monitoring (IEQ Credit 1); 2. Indoor C
Calculating CO2 Concentrations in a Zone
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Marcio Alberto Casado Pereira on
Hi! I'm finishing a project and must indicate the levels to be configured in ppm CO2 sensor environments. As an example, I have a training room with 8 people and an area of 497.29 sf.
What is legally binding language?
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Pawel Krawczyk on
A copy of the lease agreement that has been provided for review states that the tenants must install CO2 sensors in all densely occupied spaces. For the review team, it is unclear how the provided
Lease Agreement an option to comply with the credit requirements
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Katherine Ann Resurreccion on
Hi, We are currently documenting the requirements for this credit and our option in order to comply is to provide a Tenant/Lease Agreement.
HVAC system's capability to accommodate CO2 sensors
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by CT G on
We are working in a CS project without any densely occupied spaces. The project contains VRF units to condition spaces and one fan supplies outdoor air to these units.
CO2 sensors in exhaust air duct
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Mathilda Jonsson on
Hello I know that the CO2 sensors shall be installed in the breathing zone of the spaces.
NO DENSILY OCCUPIED SPACE IS AT OUR PROJECT
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Michael E. Edmonds-Bauer on
Our project is a CS building with only a few areas within the reach of control of de developer, basically the building staff offices and they will never reach 25 people per 1000 sqft. Does this me
summary for mechanically ventilated spaces
CS-2009 IEQc1:Outdoor Air Delivery Monitoringposted by BH . on
So briefly (for C&S mechanically ventilated spaces): For densly occupied spaces we need: CO2 monitors and i.e.