Tab 6-1 and 6-4

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Francesco Passerini  on 

Art classrooms are considered both in Tab. 6-1 and in Tab. 6-4. If we respect Tab. 6-4, could we avoid the verification of Tab. 6-1 (i.e. could we avoid the outdoor air supply)?

1
Thu Apr 20, 2017, 3:37 pm

Natural ventilation openings' control

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Ricardo Sá  on 

According to ASHRAE 62.1 - 2010 User's Manual, example 6-AF, the requirement associated with controls that guarantee that the openeings remain open during occupancy can be met with an administrativ

3
Default Avatar
Director of Sustainability
Edifícios Saudáveis Consultores (503 910 767)
LEEDuser Basic Member
79 thumbs up
Thu Aug 31, 2017, 6:26 pm

62MZ calculator in version 4 LEED

NC-v4 EQp1:Minimum indoor air quality performance
posted by  robert feduik  on 

Has this calculator been changed for use in NC-v4 EQp1 versus the one used in LEED 2009? For new construction, are there any other prerequisites or credits that require the use of this tool in th

4
Mon Jul 10, 2017, 11:38 am

Zone Air Distribution Effectiveness

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Francesco Passerini  on 

In the office the air (cold in summer, warm in winter) is both wall supplied and ceiling supplied. The air is exhausted from the WCs.

2
Fri May 5, 2017, 2:21 pm

Exhaustion rates in WC

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Maria Matos  on 

Dear all, I would like to know if it is mandatory to comply with minimum exhaust rates indicated in TTABLE 6-4 Minimum Exhaust Rates from ASHRAE 60.1 -2010.

3
Thu Apr 20, 2017, 3:34 pm

High Rise Residential with mixed mode ventilation

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Nancy Henderson  on 

We have several high rise residential projects that use a several conditioning and ventilation system.

3
Default Avatar
Managing Member
ArchEcology, LLC
LEEDuser Basic Member
67 thumbs up
Thu Aug 25, 2016, 9:50 pm

monitoring

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Francesco Passerini  on 

Is the monitoring of mechanical ventilation always mandatory or do exceptions exist? Regards

4
Sustainable Infrastructure Engineer
City of Calgary
LEEDuser Basic Member
2 thumbs up
Fri Mar 4, 2016, 8:41 pm

jet fans

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Francesco Passerini  on 

Table 6.4 of ASHRAE 60.1-2010 states that parking garages that don't have walls that are at least 50% open to the outside shall have mechanical air extraction (exhaust ventilation).

2
Tue Feb 23, 2016, 11:35 am

Single supply system

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Gustavo De las Heras Izquierdo  on 

Does anyone know a definition for "single supply system". I've looked it up in ASHRAE 62.1 and ASHRAE's Manual and I wasn't able to find it.

3
Tue Feb 16, 2016, 11:24 pm

Section 6.4.1.2, crossed ventilation

NC-v4 EQp1:Minimum indoor air quality performance
posted by  Gustavo De las Heras Izquierdo  on 

I don't know how to interpret the following section of ASHRAE 62.1-2010: "6.4.1.2. Double side openings.

2
Senior Sustainability Manager
WSP - Built Ecology
LEEDuser Expert
188 thumbs up
Fri Nov 13, 2015, 11:49 pm