Post a question or comment
Credit Filters
Minimum Energy Performance
Filter by location
Forum
Topic
Replies
Recent

Process Energy Savings, Alternative Compliance Path

NC-2009 EAp2:Minimum Energy Performance
posted by  Santiago Rodriguez  on 

Dear forum, We are working with an industrial plant that is seeking to obtain the LEED Certification.

3
Fri Sep 13, 2013, 4:24 pm

Basleine Fan Power credit for an exhaust fan linked to Furnace

NC-2009 EAp2:Minimum Energy Performance
posted by  Matt Scott  on 

I have an attic that is heated only with a Gas Furnace.

4
Manager, LEED
USGBC
LEEDuser Premium Member
26 thumbs up
Wed Sep 11, 2013, 1:59 pm

Return Fan included in Baseline Fan Power Calc?

NC-2009 EAp2:Minimum Energy Performance
posted by  Matt Scott  on 

Another question regarding the baseline fan power calculation in the Tables 1.4 Excel spreadsheet: Does the calculation account for the possibility of a Return Fan in the proposed system?

4
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Tue Sep 10, 2013, 7:48 pm

Energy modeling - Adjacente building

NC-2009 EAp2:Minimum Energy Performance
posted by  Luana Bertoletti  on 

Hi, I have a doubt when modeling proposed and baseline building.

6
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Tue Sep 10, 2013, 6:47 pm

Natural Conditioned Environment

NC-2009 EAp2:Minimum Energy Performance
posted by  Marina Andrade  on 

Hi! how can I prove that an environment is naturally conditioning? I believe this is not only proven by percentage of openings, correct? For example, how to prove this in a restaurant?

4
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Tue Sep 10, 2013, 4:03 pm

Baseline System 1 Pump Energy

NC-2009 EAp2:Minimum Energy Performance
posted by  Wes Lawson  on 

We are putting together a baseline of a high rise residential building. In Appendix G, it states that we need to use 19 w/gpm.

9
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Tue Sep 10, 2013, 2:00 pm

Baseline building requried to have demand control ventilation?

NC-2009 EAp2:Minimum Energy Performance
posted by  Matt Scott  on 

Per 90.1-2007 section 6.4.3.9 "Ventilation Controls for High-Occupancy Areas" systems are required to have DCV given certain criteria.

8
Default Avatar
Engineer
N.E. Fisher & Associates, Inc.
LEEDuser Basic Member
12 thumbs up
Mon Sep 9, 2013, 3:37 pm

Multiple Buildings

NC-2009 EAp2:Minimum Energy Performance
posted by  Paula Hernandez  on 

Hello to everybody, I have to model multiple buildings in a field, it´s not a campus, but three of four buildings, some of which are served by the same group of chillers. As I understand, the ener

2
Principal
Integrative Sustainability Solutions
LEEDuser Premium Member
46 thumbs up
Wed Sep 4, 2013, 4:08 pm

System 6 or System 8?

NC-2009 EAp2:Minimum Energy Performance
posted by  Rob Watson  on 

Our building is 7 floors above ground with a conditioned basement and is about 70K ft2.

2
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Thu Aug 22, 2013, 8:16 pm

Process energy? Exhaust Fan to relieve electric transformer heat

NC-2009 EAp2:Minimum Energy Performance
posted by  Matt Scott  on 

Our project has several spaces with electric transformers where we are using an exhaust fan and an outside air louver to relieve the heat loss from the transformer.

2
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Tue Aug 13, 2013, 6:39 pm