VRP calculations for fan-powered boxes using 62MZ calc

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  tiantian zhou  on 

Our system has fan-powered VAV boxes. The first review comments required us to use 62MZ calc to account for local recirculation. But we have 120 AHUs and hundreds of zones.

1
Fri Apr 11, 2014, 7:57 pm

Formaldehyde

posted by  Scott Siegel  on 
1
Mon Nov 16, 2009, 12:43 am

Exhaust System test for pressurized buildings with no exhaust

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  Alice Cook  on 

Hi all, We have an existing building built in the early 1900s with three 100% make up air units supplying fresh air with no exhaust.

1
Tue Jun 19, 2012, 3:02 pm

10 cfm per person rule

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  Jay Murray  on 

I have a small tenant space in a large high rise commercial building.

1
Thu Jul 17, 2014, 1:01 am

10% exemption?

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  Alice Cook  on 

I'm unclear if 10% of space can be exempted for this prerequisite. Could someone clarify this? We have a project where we have several retail spaces on the ground floor of an office high rise.

1
Tue Feb 8, 2011, 1:37 pm

IEQp1 Table. Case 1

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  Robert Calloway  on 

I am working on the IEQp1 LEED form and ran into a couple problems when filling out the information.

1
Tue Dec 6, 2011, 8:38 pm

Natural Ventilation vs. Exhaust Rates

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  Jan Hesse  on 

We are working on an office project that is natural ventilated in whole. All occupied spaces fullfill the requirements for natural ventilation of ASHRAE 62.1.

1
Tue Aug 6, 2013, 4:34 pm

Ventilation rates for manufacturing facilities

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  Omar Delgado  on 

I'm analyzing a manufacturing plant which is 70% manufacturing space and 30% warehouse. Do I need to follow the ACGIH Industrial Ventilation Manual to comply with this credit ?

1
Wed Mar 4, 2015, 3:15 pm

Critical Zone Identification

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  sanjay vashishtha  on 

We are doing a project in which building is of office type and is having 75 AHUs and each AHU is serving one specific tenant area, means there are 75 tenant. Each tenant area is almost 10,000 SF.

1
Fri Dec 14, 2012, 7:10 pm

High Rise Building with 120+ AHUs

EBOM-2009 IEQp1:Minimum IAQ Performance
posted by  Mark Daub  on 

Hi, Im working on a project in Germany that consists of two high rise buildings with 30 floors each. Each floor is devided into 2 Zones.

1
Tue Oct 15, 2013, 7:14 pm