Furniture heights
CI-v4 EQc8:Quality viewsposted by Subramaniam Chandrasekaran on
exactly same as the below mentioned point; for a project, the interior designer wants to know whether they have to go with 1050 mm or 1100 mm of workstation height; this clarification answers; but
compliance for naturally ventilated spaces
NC-v4 EQp1:Minimum indoor air quality performanceposted by Poorva Keskar on
Referring to the FAQs fan-assisted ventilation in naturally ventilated spaces can be considered as mechanical ventilation.
How to get the benefit of automatic shading control device
NC-2009 EAc1:Optimize Energy Performanceposted by Yusuf Turab on
We are using Visual DOE 4.2 software for energy modeling and we are doing one LEED NC project, the project team is planning to do the automatic sensor control window shading device, and how to take
Accidentally Opened Awarded Credit during Appeal Stage
posted by Bernard Sagaiyaraj on
My team member accidentally opened 2 awarded credits during the Appeal Stage for some other non-compliance credits. No changes were made to the form.
Option-3: Irrigation Meter Installed
EBOM-v4 WEc1:Outdoor water use reductionposted by VISHESH AGARWAL on
i am working on the project where project team use the STP Non potable water used for irrigation purpose. so i am reducing the 100% potable water. can i sufficient to achieve this credit.
Project located in a building with a very low fresh air rate
Retail-NC-v4 EQp1:Minimum indoor air quality performanceposted by Valentin Grimaud on
What if the project is located inside a 30-year old building with AHU supplying less than 10% fresh air rate? As we have to use the centralized ventilation system and we couldn't make any change t
WE Credit 4.2: Cooling Tower Water Management- non potable
EBOM-2009 WEc4:Cooling Tower Water Managementposted by satheesh M on
The project’s cooling requirement is being met by both chiller plant inside the project boundary as well as the chiller plant in the Building Owned DES.
Amenities Within Main Building
posted by Aswin M on
We have a Retail Commercial Interior project inside a Main building.
Modeling OA with Demand control ventilation
CS-2009 EAp2:Minimum Energy Performanceposted by Indochine Engineering VN on
Hi, I have demand control ventilation for every AHU.