FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

3 types of glass in the proposed design

In the building we are modeling 3 tyes pf glass (3 different U values and SC) are used by the architect.Is it acceptable for EAP2 that I do the following: 1-Use % or glass on each elevation provided by the acrhitect( i am iusing equest) and i think this is easiest solution than adding manually each glass because the pattern is very cmoplicated...how is the leed review is going to check the glass distribution ( which report he will ask to be provided?) 2-In the baseline i Took the total percentage of glass provided by the achitect and I assumed it is a single glass so i can have same distribution in the baseline. regards, Tarek

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/08/2012 - 13:47

1. The glazing distribution in your models should be representative of the actual design. It is OK to deviate slightly as long as the orientation and window area are basically the same and any differences would not have an impact on energy use. 2. The baseline should be the same unless the the actual overall window-to-wall ratio is greater than 40%. If it is the baseline must be modeled at 40%. The baseline windows can use the same performance parameters assuming that the framing type is the same. If you have some curtainwall/storefront and some windows the baseline values typically differ and you would need two baseline glazing performance values.

Fri, 06/08/2012 - 14:10

Marcus, Thank you again and again for your support. allow me to ask this additional question: 1-how will the leed reviewer ( and me eventually verify ) if the software (equest) is gona generate the same percentage of glasses is there a specific report I ( he ) will look for.

Fri, 06/08/2012 - 15:04

In eQUEST the DOE2 report that confirm the input data in the model is the LV-D report.

Fri, 06/08/2012 - 15:17

i agree with you but against what the leed reviewer will verify i will only provide him the total % of glass? am i right

Fri, 06/08/2012 - 15:42

Correct you are only required to enter the total % window-to-wall area in the appropriate Section 1.4 Table.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.