Forum discussion

NC-2009 IEQc4.1:Low-Emitting Materials—Adhesives and Sealants

Air-supply plenum

For an office application we have an air-supply plenum for conditioning the space, what is the maximum content of VOC allowed for the plenum sealing material? Thanks in advance.

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sun, 05/22/2016 - 13:41

USGBC addressed duct sealants in LI#5241 (http://www.usgbc.org/leed-interpretations?keys=5241): “Project teams may classify duct sealants under ‘Other’, as listed in the SCAQMD VOC Limits table.” For “Other” sealants SCAQMD-1168 allows up to 420g/L. This LEED Interpretation aligns with a previously issued technical bulletin from the Sheet Metal and Air Conditioning Contractors’ National Association (SMACNA).

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.