FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

ASHRAE 2007 G 3.1.1 Exception B

I am working on a retail project with three restaurant spaces. I got a comment below from the LEED reviewer. 

"The General HVAC and Air-Side HVAC tabs indicate that system type 6: Packaged VAV with PFP Boxes is the only system type
in the Baseline model of the main building; however, it appears that this building includes spaces (such as restaurant/cafeteria
space, etc.) that may meet the requirements of exception (b) to Section G3.1.1, which require an additional system type to be
reflected in the Baseline model. An additional system type must be reflected in the Baseline model if an exception to Section
G3.1.1 is met. If exception (b) to Section G3.1.1 is met, revise the Baseline model of the main building to include an appropriate
additional system type for space where required. In addition, update the General HVAC and Air-Side HVAC tabs and provide
the SV-A report reflecting the changes." 

Are the exceptions mandatory? Since I am getting unmet hours when I am claiming the exception, can I not claim it? 

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 05/23/2020 - 17:43

Yes they are required, refer to General HVAC tab row 49 "All applicable baseline exceptions to G3.1.1 have been implemented. Note that these exceptions are required, not optional" Unmet hours are not related to the additional systems. Section G3.1.2.2 explains more about the unmet hours. I think if you can show that the thermal load and  the schedules of the restaurant does not meet the requirements of exception (b) you can keep the model with one system.

Tue, 05/26/2020 - 18:50

Hi Jonathan, Siaf is correct. If the project includes other space types (offices, other retail, etc), this comment is not unusual. Note that the internal gains at cooling design conditions include all internal gains (people, equipment, lighting, and ventilation loads), and usually spaces such as kitchen, dining room, auditorium, etc. often qualify based on the load and/or schedule difference. If an alternate system is not required, your response should clearly indicate why and include calculations. Cam

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.