FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

ASHRAE contradictory with local standards

Hi, we have a project in a country where local requirements set high standards for legionella protection, thus there are high requirements regarding the water temperatures and water circulation. Requirements are in contradictory with the ASHRAE mandatory requirmnets . How to deal in this kind of situations? Are there any exceptions from ASHRAE 90.1-2007? Thx

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 06/23/2014 - 13:10

Could you be more specific? Which mandatory provision(s)? The exceptions are already listed in 90.1. Any other exceptions would be in addenda or in the LEED Interpretations.

Tue, 06/24/2014 - 08:05

7.4.4.2. ; 7.4.4.3. and 7.4.4.4

Tue, 06/24/2014 - 12:52

7.4.4.2 - if you can make the case that hot water is always required then this control requirement would not apply. 7.4.4.3 - much more than 110 will burn someone. Seems like a simple fix to mix hot water to bring down temperature. 7.4.4.4 - if these controls operate 24/7 then again this would not be required