FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Balancing Devices to meet ASHRAE 90.1 Mandatory Requirements

We have a project that is an industrial facility, it shares the CHW distribution piping between the comfort system and the process system. We are informing the CxTeam that it is required to have balancing means at all connected devices, and/or at a minimum at all comfort devices and each branch going out to the process part of the CHW distribution piping. The owner has CHW flow diagrams indicating the required gpm for their process, including future expansion. Our "requirement" to the owner is to install balancing or flow limiting devices at the process branch piping to be able to meet the requirements of section 6.4.5 and subsequently 6.7.2 of ASHRAE Standard 90.1-2007. Any comment regarding our "requirement" is appreciated. We do not want to obligate the owner to do something that is not a Mandatory Requirement, but we also want to make sure that these are met. Thanks Jorge

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/30/2015 - 15:56

Your requirement makes sense to me and also just sounds like a good design practice. If your system can be hydronically balanced without this valve then it would not be mandatory. So the best answer is it depends.