FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Baseline Chilled water pumps - G3.1.3.10

Greetings, The standard states that the pump power must be 22 W/gpm. If the project has two chillers and primary secondary circuits, whereby there is on pump per chiller in the primary circuits and 5 pumps in the secondary. The question is: the 22 W/gpm are covering which power as per the above description? The similar question is valid also for G3.1.3.11 and G3.1.3.5. All opinions on the matter are highly appreciated. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 05/02/2016 - 15:23

The number of chillers and pumping in the proposed case has nothing to do with the baseline. There is an ASHRAE interpretation - ASHRAE/IES IC 90.1-2007-14 - which indicates that the Baseline pump power of 22 W/gpm from Section G3.1.3.10 is inclusive of all baseline chilled water pumps. This ruling is confirmed by LEED Interpretation 10299. For G3.1.3.11 and G3.1.3.5 it is a moot point as there are only primary pumps for towers and boilers.