FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Baseline, section 6.4.3.9 and G3.1.1, single zone system

Dear all, I have an office building with an auditorium, which is served by the same AHU that serves the surrounding office. The question is how to model the system for this zone in the baseline building. My main baseline system is 7. G3.1.1, exception b -> I need a separate system 3 or 4 (CAV) for this single zone, as the occupancy is more than 31.2 W/m2 higher than typical other zones. 6.4.3.9 -> the zone is > 50 m2, has a higher occupancy than 40 P/100 m2 and the baseline main system has an air-side economizer (S7), therefore demand controlled ventilation required BUT, according to the exceptions, I do not need a DCV, as I have a system with exhaust energy recovery of min. 50 % Conclusion: model the auditorium zone separately with system 3 or 4, constant air volume, without demand controlled ventilation. BUT, when I check the excel sheet tab "general HVAC", I find the point: Demand control ventilation is modeled in the baseline case for all spaces larger than 500 sq ft (50 sq m) that have a design occupancy for ventilation of greater than 40 people per 1,000 sq ft (100 sq m) of floor area (except for spaces served by baseline systems that do NOT have one of the following: an air-side economizer, automatic modulating control of the outdoor air damper, or a design outdoor airflow of greater than 3,000 cfm (1,400 L/s)) per G3.1.2.6 / 6.4.3.9. -> this says for me the opposite as section 6.4.3.9 itself? How should I model the auditorium? Thanks! Sarah

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/03/2017 - 14:55

Sounds like G3.1.1 exception b applies so you would model a separate system for the auditorium. Is your separate system required to have heat recovery according to G3.1.2.10? If so then you are correct no DCV in the separate baseline system. If not then you do need to include DCV. Sounds like a mistake in the spreadsheet. As you point out they are not listing the exceptions, they are listing the listing the conditions where it is required.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.