FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Baseline System for Warehouse Shell

Wondering how to determine the baseline system for a warehouse that upon initial completion will be a cold, dark shell maintained at 50°F. For EAp2 we are assuming 10% office space for the future tenants and use of PSZ-AC units for those spaces. The remaining 90% is assumed to be warehouse space that will be only heated to maintain 50-60°F. How do I apply the system mapping of Table G3.1.1A to this building? Since the building is 200,000 SF and utilizes fossil fuels for heating, the table indicates System 7 – VAV with reheat. So would I apply that baseline system to the entire building or just the office spaces? If just to the office spaces, what would I use for the warehouse? The proposed model will have make-up air units and unit heaters in the warehouse. Would appreciate input anyone may have. Thanks,

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/14/2012 - 22:35

Sounds like the predominant condition (see note under Table G3.1.1A) is the warehouse. It does not really matter what happens on initial completion in a CS project. All the spaces are modeled as if fully occupied. If you do not know the occupancy you will need to ask the owner what the space is intended for and model that based on assumptions found in the energy modeling appendix for CS projects in the Reference Guide. If the systems are not designed then they are modeled the same as the baseline in the proposed. If they are designed then the proposed is modeled as designed. Of use in selecting your baseline system will be the exceptions to G3.1.1 which allow a secondary system for the office area. The warehouse itself may qualify as a system #9 or #10 from ASHRAE 90.1-2010 if the space is heating only.

Wed, 08/15/2012 - 17:31

Thanks Marcus. I appreciate the input. I think you’re right that system 9 from ASHRAE 90.1-2010 would be appropriate to use here. The only HVAC system that will be designed as part of the C&S scope is the gas unit heater system which will heat the entire building upon initial completion and only the warehouses once the tenants are built out. It makes a lot more sense to compare this to system 9 than to system 7. So that covers comparison of the designed elements to the baseline as determined by 90.1. For the offices I will use system 4 - PSZ-HP for both the proposed and baseline models since those systems are not yet designed. This approach makes the most sense to me since it allows documentation of energy savings for the designed system (if any), and leaves the undesigned area neutral. Thanks for all your help!

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.