Forum discussion

CS-2009 IEQc8.1:Daylight and Views—Daylight

Basic Manual Shades

Can basic manual operated fabric shades be used for areas that are above 500fc? Something such as a Draper Manual Flexshade? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 07/18/2014 - 12:55

Yes, there is no specific requirement as it relates to the VLT of the shades. However, use of manual shades does not allow projects to not consider values over 500fc in their calculations. The areas over 500fc will be considered as not being properly daylit. Only the use of automated shades will allow you to do this.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.