CS-v4.1 EAp2:Minimum Energy Performance

Category of cooling for process load

How should I categorize the cooling required for IT equipment in data halls. Considering that the cooling in the actual building is provided by air cooled chillers, which are listed in Table 6.8.1-3 of ASHRAE 90.1. Can I assume that, they are not process load and determine the COP based on table G3.5.3. Regarding the number of chillers does it need to be as identical as proposed building.  

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/03/2021 - 16:09

They are a process load. Table G3.5.3 is the efficiency required of the baseline system. The number of chillers is determined by Table G3.1.3.7.

Thu, 06/03/2021 - 16:22

Do you mean that, the cooling for the IT equipment is process load and should be identical in both baseline and proposed building?

Thu, 06/03/2021 - 16:35

Sorry the IT equipment is clearly a process load. The cooling for it generally is not.