FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

CHP system

in the project we are modelling, hot water system is preheated from the building power generators by using recovery system isntalled on the genertars ( same principle of the recovery chillers) but the saving is much higher. The problem in my opinion is that :in my country the power go off 3 hours daily so the generators will run 3 hours daily and the saving ( as per supplier can be up to 30%) due to the high temperature of water used to preheat the hot water system which otherwise would be cooled by the generator cooling system and wasted to the atmosphere. does USGBC accept my calculation based on 3 hours run per day?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/27/2012 - 12:59

Heat recovery from a generator should be acceptable. You will need to account for the fuel to run the generator in your modeling.

Wed, 06/27/2012 - 13:06

thank you for your reply As I checked in equest,The generator heat recovery will be modeled based on the fraction of heat recovered and not based on the time the generator runs is this acceptable or I need to show more information?

Wed, 06/27/2012 - 14:17

Sounds odd to me. Since you can only recovery heat when the generator runs I am not sure how you get energy saved just on a fraction of heat recovery.

Wed, 06/27/2012 - 14:20

lets consider it as efficiency of the heat recovery system. My question is how do i need to specify how many hours the generator run. have you ever used this system before in equest ( i tried over the net specially www.onebuilding.org) but nothing can you tell me how should i simulate that ?

Wed, 06/27/2012 - 14:41

Not sure off the top of my head. We would have to research that one. t d - since you frequently post here any chance we could see your actual name?

Wed, 06/27/2012 - 15:09

sure,But if equest can model this system do i need to provide further documentation. and another question ashrae point 6.5.6.2.1 but the dominant baseline system is PTAC how can i recover the heat if system 8 ( offices ) what will i do if the DWH system load is bigger than the cooling tower size? shall i recover 60% only as mentioned in the point? what if heat rejection is less than 60% of DHW what shall i do?

Wed, 06/27/2012 - 18:13

If eQUEST can model it you should not need much further documentation but it is often a good idea to explain how complex systems have been modeled to help the reviewer understand. 6.5.6.2 applies to chillers not generators. It is a prescriptive measure so your Proposed design is not required to do this but your Baseline would if the criteria listed apply to the Baseline. 6.5.6.2.2 addresses the capacity issues. Nice to know your name, thanks.

Wed, 06/27/2012 - 18:37

I know it applies for chillers so what shall i do if in baseline only offices which constiture only 20% are cooled by chiller while the 80% is residential and is cooled by PTAC what can i do?

Wed, 06/27/2012 - 19:00

The criteria only applies to the chiller portion of the building.

Wed, 06/27/2012 - 19:42

Thank you ,after your answer I read again the clause and i didnt find it terrifying as I thought in the begining ...Just to satisfy my curisority what is the highest LEED certified building in the world does anybody know

Wed, 06/27/2012 - 20:04

First rule of energy modeling don't panic when you don't understand something right away, you will be in panic all the time! :-) Tallest or most points?

Wed, 06/27/2012 - 20:06

Now you are telling me this :) i meant tallest or how many floors?

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.