FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

is this clarification ok?

automatic daylighting controls and occupancy sensor are adapted into the project, and many other energy saving measures included,i do not simulate daylighting control and occupancy sensor in the energy model for the first submittal, because my project requirement is just 10% cost saving and i achieved 14.3% cost saving by other energy efficiency strategies. the reviewer comments require that i provide a narrative describing the controls and how they are implemented in the Proposed energy model. can i answer " i did not model automatic daylighting controls and occupancy sensor in the energy model based on my project certification goal?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/11/2014 - 14:48

You are required by Appendix G to model the project as designed which includes all of the strategies in the design (Table G3.1-1). Your percent savings goal really has nothing to do with the issue so I would not even bring it up. Even though you are required to model the project as designed/constructed, you are permitted to exclude certain design features if you can demonstrate that not modeling them results in a conservative estimate of savings. In other words you are just hurting your savings so that is typically allowed. So I would just explain the the reviewer the lighting controls and how they were modeled. Make sure you have properly addressed any control issues which are also mandatory provisions (like 9.4.1.2) as these are required no matter your percent savings.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.