FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

COP and SFP values for energy modelling

(for a office building in Sao Paulo) COP: For an office building in Sao Paulo, the proposed case uses air cooled system with a COP value of 2.87. The base case calculation from table G3.1.3.7 and table 6.8.1C of the 90.1 standard gives us a COP of 5.50 (i.e. assumes a water cooled chiller). Does that sound correct ? Is there a case that the baseline building utilises an air cooled chiller of a COP of 2.8 for the purposes of the baseline assessment? Or is there any other way of calculating the COP of the base case except complying to the above mentioned ASHRAE tables? SFP (Specific Fan Power): We got a supply (and extract) flow rate of 60,142 L/s for our building ( calculated from the equation). With the power consumption of fan blower at 108 kW, we get a SFP for supply of 1.80W/l/s. The same applies for the extract fan – i.e. SFP of 1.8W//s. This totals to a combined supply and extract SFP of 3.6 W/l/s, which is significantly higher than the maximum permissible standards that we generally in the UK – i.e. limiting combined SFP value of 2.4 or less) Can anyone advise on this ? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 04/30/2013 - 13:35

COP - Assuming you have correctly selected the baseline system (7 or 8) then yes it sounds possible. It all depends on the correct identification of the baseline system. SEP - Is this for the baseline? If so all the fans (supply, return, relief and exhaust) associated with the system are included in the calculations. So maybe you are double counting? There is a spreadsheet in the Documentation Toolkit tab above that does the fan power calculations to double check your work. The supply flow rate is auto-sized by the modeling software right?

Wed, 11/18/2020 - 14:41

SPF is specific (i.e. normalized to the volume flowrate). It's not additive. You are supposed to make a volumeflowrate weighted average.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.