FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Dehumidification + reheat

In the designed AHU a cooling coil operates also in order to control the humidity ratio. During the summer season, because of the required dehumidification after the cooling coil the air temperature can become uncomfortable (16°C or even less). To avoid discomfort for the occupants, after the cooling coil there is a reheat coil. The reheat coil controls the supply temperature, which should be about 20°C. The cooling loads are balanced by radiant floors. Since the building is going to be used for healthcare purposes (in particular for seriously ill people), avoiding discomfort conditions is very important. I think that in the proposed model I shall consider such a control strategy. Since reheating causes an energy demand increase, I am wondering whether I could consider it in the baseline model. Shall dehumidification and reheating be modeled identically in the proposed model and in the baseline model? The baseline system is System 3 – PSZ-AC. Best Regards

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/22/2015 - 18:00

ASHRAE 90.1 Appendix G is unclear in how to appropriately account for humidity (both humidification and de-humidification). As stated in ASHRAE 90.1 Table G3.1.1 (b), all conditioned spaces shall be modeled with temperature and humidity control setpoints the same for the Proposed and Baseline Case, however there is no other guidance/requirement for modeling humidity. Humidification should therefore be modeled the same in the Baseline and Proposed Case unless an Exceptional Calculation Method is used. The Exceptional Calculation should justify the use of the Baseline (including evidence for what is standard practice in the project location for the type of application). It is not always possible to model identical forms of humidity control. In that case, it is recommended that the same fuel source for humidity control be modeled in the Baseline and Proposed Case. For example, if electric reheat is used, that would be modeled in both cases. If fossil fuel is used for humidity control, that would be modeled in both cases. You should provide additional justification if including reheat in the baseline.

Wed, 09/23/2015 - 06:56

This is a great thought provoking question. Comfort vs. energy savings. Which is more important?! I think the incentive to save energy is already well established. If ASHRAE in this case would refuse to make the baseline reheat, it is saying that user comfort should be degraded to save energy! I don't think that is a good approach. In the LEED system we will punish the design for bad comfort, but do we punish the baseline also? In the spirit of LEED I would make the baseline reheat and make my case to the reviewers. Perhaps, this is something for the 90.1 commitee to consider that as much as you may want to seperate 55 and 90.1 to do their respective jobs, sometimes you just can't.

Wed, 09/23/2015 - 09:45

Thank you for your answers. I have considered another aspect: including reheat in the baseline could be impossible because of control problems. I mean, System 3 is CAV, i.e. the zone air temperature is controlled only through the supply air temperature (there is no possibility to modulate the air flow rate). If I reheated the supply air, the setpoint zone air temperature could be unreachable. I'm going to see how much the reheat is important (from the point of view of the energy requirements) in the proposed model. Best Regards

Wed, 09/23/2015 - 09:52

Yip. Try and see if you can "cut it off" onto a seperate system using one of the exceptions. So like if a zone sees very different occupation schedules, but hangs onto the same system, you could have the baseline serve it with a different system. Similary, there are exceptions for schedules regarding loads, outdoor air requirements, and so on.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.