FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

District heating and cooling

I am going to model a building that is connected with a district heating/cooling system. I’m going to use the simplified option of the document “Treatment of District or Campus Thermal Energy in LEED V2 and LEED 2009 – Design & Construction” (i.e. the Building Stand-Alone Scenario – the building is treated separately from the DES; all upstream equipment is ignored). Since the system is of the same owner of the building, the energy is not paid by the manager of the building, but by the manager of the district system (and the situation is the same for all the buildings that are connected with the district network). Therefore the cost of the energy that is exchanged between the network and the building is not considered. The management of the system buys natural gas, but I don’t know the efficiency of the systems, which are very complicated and we want to avoid to model them. I see two possible solutions: 1. I consider standard prices for purchased heated/chilled water for the region. 2. I don’t consider the energy cost, but the primary energy. Are those solutions acceptable? In both cases I would consider the same values for the baseline model and the design model. With Regards Francesco Passerini

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 07/13/2016 - 18:48

Follow the guidance in DESv2 Section 2.4.2. Based on that the guidance to your options is neither.

Thu, 07/14/2016 - 11:13

Hello, Marcus. Thank you. It seems that I’m misunderstanding something. I’m considering p. 14 of DESv2. Units of $/MBTU = Virtual Electric Rate (in $/kWh) x 71 If the cost of the electric energy is 0.10 $/kWh then the chilled water cost shall be considered 7.1 $/MBTU, i.e. 7.1/0.293 = 24.23 $/kWh.

Wed, 07/20/2016 - 14:56

MBTU = million BTU not thousand BTU The 71 constant includes the conversion to BTU and the default efficiency of the central plant.

Wed, 07/20/2016 - 15:35

Therefore the cost shall be divided by 1000: 0.024 $/kWh. Thank you, Marcus.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.