FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Does 10-4 Mandatory provision apply for process electric motors?

Dear community, I would like clarifications about the scope covered by the section 10-4 of the ashrae 90.1-2007: in an industrial project, there may be lots of electric motors related to the industrial process. Must these motors comply with the minimum efficiency requirements of the table 10.8? Thanks for your clarifications,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 04/01/2013 - 19:46

I think that only motors that are used for regulated purposes of the 90.1 Standard are covered by 10.4. So industrial motors would not have to meet all of the requirements.

Tue, 04/02/2013 - 10:54

it is really mandatory to comply with section 10-4 of ashrae 90.1-2007 if building simulation is choosen to comply for EAP2?. If building efficiency comply with required percentage (5-10%) although electric motors efficiency is less than that in table 10.8, it is valid? For projects and eelectric motors in Europe there is no other standart aplicable instead of NEMA? IEC 60034-30:2008 or EN/IEC 60034-2: 1996 standart are not valid? There is not other rpm values? for table 10.8, usually it is work with 50Hz in Europe. There is no ASHRAE compliance form, for this mandatory requirement?

Tue, 04/02/2013 - 13:21

LEED project must comply with the mandatory provisions and show the minimum percent savings. I am not aware if the European motor standards have been granted equivalency or not. To be honest, unless you point it out in the documentation, this issue would not come up on a typical LEED review. Although the electrical engineer (or other party) is stating that the project complies with the mandatory provisions.

Thu, 04/04/2013 - 10:17

Thank you Marcus, If industrial motors do not have to meet the requirements, can I still claim savings on the process energy cost if the installed motors are more efficient than what is stated in the table 10-8? In other words, can I consider these tabled efficiencies as "conventional practice"? I am referring here to the language of the table G3.1, section 12. Thanks for your clarifications,

Thu, 04/04/2013 - 13:27

Oh so you want your cake and eat it too? :-) You can claim savings but would need to do an exceptional calculation. Using these efficiencies as the baseline makes sense to me.

Thu, 04/04/2013 - 14:10

Shouldn't the local conditions be considered? I mean, ASHRAE documents are conventional practice for the United States, but in other countries other documents should (shall?) be considered, shouldn't they?

Thu, 04/04/2013 - 14:40

Yes they should. So if the local country or region has a set of standards that is reasonably equivalent to the US-based ASHRAE standards you can always make the case for using the local requirements and practice.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.