FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

EAp2 Section 1.4 tables.xls

I am in need of help with EAp2 Section 1.4 tables.xls. This project is for new construction. 1. What means “Semi-conditioned”? The storage space has only heating and ventilation, is this means “semi”? 2. “Unconditioned Total Fan Power”, is it fan for parking garage? According to ASHARE 90.1-2007 parking garages with natural or mechanical ventilation are not considered enclosed spaces. Therefore it is not “unconditioned space”. 3. The baseline case is with system 8 and the cooling load is lower than 300 tons. I choose the COP for chiller from table 6.8.1.C. Is it wrong? According to “EAp2 Section 1.4 tables.xls“ Efficiency should be from tables 6.8.1A, 6.8.1B, or 6.8.1D. The baseline heating Type is electric resistance, which table (tables 6.8.1B, 6.8.1D, or 6.8.1E) should I use? Thanks!

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 05/23/2011 - 13:35

Semi-conditioned is defined in the beginning of the Standard under "space". Again refer to the defintion of space - an enclosed space can also be unconditioned. That is the correct Table (6.8.1C) for a screw chiller in the baseline. Enter the efficiency values in Table 1.4.3 HVAC Water Side. I think it is an omission in the form to not include Table 6.8.1C. There is no table for electric resistance heating. Its efficiency is always 100%.

Wed, 05/25/2011 - 13:48

Thanks Marcus. But I did not quite understand. Is “Semi-conditioned” the same as “semiheated space” in ASHARE? And I have another question for “G3.1.3.12 Supply Air Temperature Reset” How to calculate the supply air temperature resetting, if the max room temperature is 26.5 °C? What means “the minimum cooling load conditions”?

Wed, 05/25/2011 - 20:30

Sorry for the confusion. I am using semi-conditioned and semi-heated as the same term. This section refers to the supply air discharge temperature, not the room temperature setting. The supply air temperature is reset up to 5 degrees F above design temperature if the cooling load can be met with the warmer air. This serves the purpose of reducing the reheat requirements in other spaces served by that system.

Thu, 05/26/2011 - 09:32

Thank you for the reply again. Bellow I have described how I caculate my Baseline Case, please would you correct this. There are 5 AHU systems in proposed case for Office, Restaurant, Lobby and Storage. The proposed systems have no return air, and supply airflow rate is the minimum outdoor air. Therefore in baseline case I calculate the fan power and the design airflow rate for each system. 1. Minimum outdoor airflow rates are identical with the proposed case (G3.1.2.5). The min OA for office is 91,200 m³/h. 2. For Office the space heating load is 192 kW and cooling load is 313 kW. The baseline airflow was calculated base on 313 kW and a delta T 20 °F (SA to RA). The result is 84,510 m³/h and smaller than min OA (91,200 m³/h). According to G3.1.2.8 the required ventilation air is larger, therefore the design airflow rate is identical with min OA. 3. The min RA is 20 °C and the max RA is 26.5 °C (79.7 °F).The SAT was calculated as follows: Tzone – Tdesign = 20 °F 79.7°F – 59.7 °F = 20 °F Treset = Tdesign + 5 °F =59.7 °F +5 °F = 64.7 °F The air temperature for cooling will be reset to 64.7 °F Thanks a lot!

Tue, 05/31/2011 - 16:56

1. yes OA must be identical 2. It is OK that the baseline would come out less than the proposed 3. The 20F delta T should be based on the cooling room temperature setting. If that is 26.5C then you are correct.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.