FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Exception b. of G3.1.1 and setpoint temperature

Exception b. of G3.1.1 states: “use separate single-zone systems (..) for any spaces that have occupancy or process loads or schedule that differ significantly from the rest of the building”. Are setpoint temperatures considered as “schedules”? Consider a floor where there are a space with cooling setpoint temperature equal to 25°C and another space with cooling setpoint temperature equal to 40°C. They have similar process loads. During many hours the first space will need cooling while the second one won’t. Anyway, if the two spaces are connected with the same system they will both be supplied with cooled air. For the space that doesn't need cooling the air flow will be at the minimum level (see G3.1.3.13), but anyway supplying a space with cooled air when it doesn’t need cooling is an energy waste. What is correct for the baseline model? Regards P.S.: as supply temperature from the central AHU I’m going to use 25°C – 11°C = 14°C, and I’m going to “reset higher by 2.3°C under the minimum cooling load conditions”, based on the outdoor temperature (see G3.1.3.12)

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 10/23/2014 - 07:49

Yes they are in my opinion. I've also come accross this issue. And yes, that is why there is a reset rule. The reset rule is basically trying to minimize the waste. You can consider it differently. The rooms with the 40 C setpoints have very different loads than those with 25 C, and there is an exception for that. So don't hang a trash room on the same air circuit as the office spaces in the proposed design, for example.

Thu, 10/23/2014 - 15:13

The temperature set points are certainly like schedules in that they need to be identical in both models.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.