FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Exception G3.1.1.c and zones with minimum air changes

Hello: I have a question related to exception G3.1.1.c which states that a separate single System 3 should be used for zones with pressurization relationships or minimum circulation rates. I have a 3 story mixed use healthcare facility with offices spaces, exam rooms, treatment rooms, research spaces, and a surgical and pre/post suite. My proposed system is chilled water and hot water VAV AHUs. My baseline system is System 5. 1. For the baseline I was intending to model a System 5 per floor and set the minimums to either 0.4 CFM/ft2 or whatever minimum air change rate is required by ASHRAE 170. I do not believe exception G3.1.1.c would be appropriate for this building because multiple zones (about 50%) have minimum circulation rates or pressurization requirements. Does this seem to be an appropriate interpretation of this exception? 2. On the first floor of my building I have a surgical and pre/post suite served by 2 different AHUs. The AHU serving the surgical suite has return terminal boxes on all of the zones whereas the AHU serving the pre/post suite does not have return terminal boxes. I was intending to model the surgical area as a separate System 5 (same zoning as proposed) and the rest of the floor as another System 5. Once again I'm not sure if this would be justifiable so any input is appreciated.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 07/19/2016 - 15:50

You must model the G3.1.1 exceptions if they apply. 1. Exception c is only applied to spaces in the building that meet this criteria. Typically a surgical suite meets this criteria. 2. See 1. You can't model a separate system 5. You can only apply one of the exceptions. If they apply you must apply them.

Mon, 08/01/2016 - 21:21

Hi Marcus: To clarify, any zone with a code minimum air change rate or a pressurization relationship is modeled as a separate System 3 (including blocks of exam rooms, pre/post rooms, etc.). I assume the minimum flow set-point for the System 3 is to be set as the the code minimum air change rate. The remainder of the zones which are not dictated by minimum air change rates are placed on a System 5 per floor. Thanks again for your input.

Tue, 08/16/2016 - 15:47

Yes if it qualifies under Exception b you model a system 3. The outside air must be identical to the proposed design (unless there is DCV in the proposed system then the baseline uses the code minimum). Yes to the remainder of zones.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.