FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Existing building reconstruction and expansion

Questions for the experts: We have a project that will have some floor areas demolished and reconstructed/renovated, and also some new construction (less than 20%). 1. We understand that for those portions of the project that will be renovated, to use the existing building as the baseline. Does this approach also apply to the reconstructed areas (e.g. floors demolished and reconstructed)? 2. For the renovated portion, do we have the option of using either the existing building, or ASHRAE 90.1 standard building as the baseline? Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/31/2016 - 15:03

1. No the reconstructed areas would be considered new construction. 2. It depends. You should use the existing conditions. You could maybe use the 90.1 minimums if you can demonstrate that they are greater than the existing condition and that doing so will produce a conservative result (less savings).

Wed, 08/31/2016 - 15:46

Thanks for the prompt response, Marcus!

Wed, 08/31/2016 - 20:32

Marcus More questions: 1. EAp2 Section 1.4 Table 1.4.7A “Baseline Air-Side HVAC Schedule” only allow a baseline system to be selected from one of eight standard ASHRAE Baseline HVAC System Types. Our existing system does not fall into any of the standard types. We have not found any reference that allows for the characteristics of an existing HVAC systems to be used in determining the baseline HVAC system. 2. We will be replacing the mechanical system entirely. Does this change our approach to what constitutes baseline? Thanks again.

Wed, 08/31/2016 - 20:38

1. The proposed system type does not determine the baseline system type. The fuel used for heating and the area/# of floors determines the baseline system. See Table G3.1.1 in Appendix G. 2. No. The Baseline is always according to Appendix G. The only exception is if you are reusing existing equipment. Then it gets modeled identically in both models.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.