FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Exterior LPD addendum i and 90.1-2010

Hi, what surface type should be used for overhang construction if using Addendum i or 90.1-2010 version? The "Canopies and overhangs" category for Tradable Surfaces are missing within addendum and 2010 Standard and I'm not sure what to use. There is only Entrance canopies category and it does not fit for my almost 16 m overhang where is no entrance. Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 01/19/2017 - 14:33

You have to use the surface type that fits the best. If it is not a sales canopy it is an entry canopy. That is the more conservative approach and should be accepted.

Thu, 01/19/2017 - 16:08

OK, now I see. Thank you Marcus.

Mon, 05/15/2017 - 21:09

Thank you for the insight, Marcus. I've been having a hard finding whether or not 90.1-2010 or LEED have given any technical definition for what qualifies as a "Sales Canopy". Any reference you know of would be greatly appreciated. So, would you categorize common parking canopies as "Entry Canopies"? Thanks!

Tue, 05/16/2017 - 14:42

I am not aware of a definition for sales canopy beyond the obvious. I am not sure exactly what you have in mind for a parking canopy but the image that comes to me would be something you might see in front of a hotel. That is usually associated with the entry to the front door so it would be an entry canopy.

Tue, 05/16/2017 - 15:52

I'm more referring to freestanding, unattached canopies, often found in the middle of a parking lot. (They're becoming a rather popular place to lay solar panels on top of these days.) Here's an example picture: http://cltc.ucdavis.edu/sites/default/files/styles/main-image/public/photos/article/1401-woodland-pv-smart-lighting.png?itok=oZUSDap9 What category would you see the exterior lighting under these canopies best fit into?

Tue, 05/16/2017 - 19:08

Parking. It does not matter if you are lighting it from a pole or a canopy.

Tue, 05/16/2017 - 19:17

Thanks, Marcus!

Tue, 05/16/2017 - 19:24

If you are lighting the parking this way (or any way for that matter) make sure to only include the area of parking/drives that meets the minimum illumination levels for parking lots.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.