FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Fan Power Calculation

Let's say we have a HVAC supply fan of a baseline which is calculated to be 3,000 cfm and the baseline fan power at 0.001 kW/cfm.This makes the fan power to be 3 kW. What if the same space has a wall mounted exhuast fan of 300 cfm. According to section G.3.1.2.9, do we have to alocate the allowance of 3kW to both supply fan of 3000 cfm and exhaust fan 300 cfm? This will make to average kW/cfm to be 3/3300 =0.00091 kW/cfm to be specified for both fans. Am I correct? Thanks

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 07/14/2014 - 13:38

The Section G3.1.2.9 calculations includes all of the fan power for that system (supply, exhaust, return and relief). You do not add them as the calculation is primarily based on the supply air.

Mon, 07/14/2014 - 13:53

So, in the baseline, there would be supply fan based on G.1.2.9 which has full kW from the calculation. the exhaust fan will have the flow (to maintahn same OA rate with the proposed) but the kW/cfm will be set to 0. Am I correct?

Mon, 07/14/2014 - 14:02

Once you calculate the total baseline fan power you can allocate it among the fans in the system. The best way to do this is proportional to the Proposed system but there is no requirement to do so.

Mon, 07/14/2014 - 14:59

Thanks, Marcus if we do the proportional fan power of the baseline. Then we just use the "supply" fan power (exclude exhuast fan power) to calculated adjusted compressor EER (system 3-4). Am I right?

Mon, 07/14/2014 - 15:49

The conservative approach would be to use the total G3.1.2.9 fan power to adjust the unit EER. If you want to use the supply fan power only based on your allocation of the fan power then you should be prepared to defend the allocation of the fan power. For example, if there is a corresponding exhaust fan in the space as you describe above and you have proportionally allocated the fan power you would be able to justify that the exhaust should be excluded from the EIR calculation.

Mon, 07/14/2014 - 15:58

Could you point me to another method besides G3.1.2.9 fan power to adjust the unit EER? or which section to read.

Mon, 07/14/2014 - 16:16

I did not look to see if it would help but the next reference to check for clarification would be the User's Manual.

Tue, 07/15/2014 - 13:32

Thanks, Marcus. By the way, if we have a kitchen heavy duty hood of a restaurant. Can we exclude fan power of the baseline using exception 6.5.3.1.1b? (mentioned if current Section 1.4 table not have to report in fan power table). Hood fan power calucation method for the baseline was mentioned in 6.5.3.1.1 as well. It seems unfair if a total allowance of baseline fan power inculded kitchen hood fan. Such fan usually consume a lot of energy in design/proposed case.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.