FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Glazing ratio

We are working with a building that has 9 floors, the first 6 floors are for parking, unconditioned naturally ventilated with no glass on the envelope, and the last 3 are conditioned office spaces with a high WWR. To model the baseline, should we consider the whole façades of the building (6 parking floors + 3 office floors) to calculate the 40%, or just the conditioned height (3 office floors)? From table G3.1-5 it seems that the whole façade should be used to calculate the WWR: "40% of gross above-grade wall area, whichever is smaller," To select the Baseline HVAC system we are considering just 3 floors, as we understand, from Marcus´ comment previously posted, that only conditioned floors count. Thanks in advance, Anderson

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/20/2014 - 21:31

I will not disagree with myself, at least this time!

Thu, 08/21/2014 - 08:23

- It has been ruled (last I heard) that parking buildings are not LEED certifiable. - It is said that the building should concider all parts that are needed for it's function...in your case I was thinking that the parking is not for the offices per say and should probably be excluded. - The WWR rule applies only to surfaces where the proposed design has glazing. You can't put glazing where there isn't any in the proposed design.

Thu, 08/21/2014 - 12:42

Clarification: On its own, an unconditioned, unoccupied parking garage is not eligible for LEED certification. However, a parking garage attached to a conditioned building and within the LEED project boundary may be certified as part of that project. In this case, all costs, materials, and activities associated with the garage must be taken into account for all credits & prerequisites. That said, the window-to-wall ratio only applies to walls that enclose conditioned space, so the walls of an unconditioned garage must be excluded from this calculation. On the other hand, for the energy models, one must include lighting, mechanical ventilation, & other loads associated with the garage, even though it is unconditioned. Is that right, Marcus?

Thu, 08/21/2014 - 14:03

You must model everything that impacts energy use within the LEED Project Boundary. You determine the project boundary within the confines of the MPRs.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.