FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

High Hazard Areas for Core & Shell

We are working on a warehouse building with attached offices in climate zone 5A, with gas-fired rooftop equipment for heating. Per Table G3.1.1, the baseline system should be system type 5, but a significant portion of the warehouse space is "high hazard," which requires constant temperature & make-up & exhaust air. Page 272 of the 2009 reference guide says to use Table G3.1.1, except areas where occupancy, process loads or schedules differ significantly from the rest of the building, so can I use the proposed system type for the baseline? If not, what system type should be used?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/14/2012 - 20:06

You will need to apply one of the exceptions under G3.1.1 and that exception will tell you what baseline system to use. You could also look at applying a system #9 or #10 from 90.1-2010 if that works for your situation.

Tue, 08/14/2012 - 20:53

The high hazard area is heated and cooled, so system types 9 & 10 cannot be used. It is 1-story and over 25,000 sf, so the baseline would still have to be type 5. The real system must be constant volume due to the type of materials being stored in this area and their associated ventilation load. Can an exception be justified through a narrative for a case such as this?

Tue, 08/14/2012 - 21:52

If G3.1.1 exception b or c is applied then it is a system 3, not a 5. The only other exception I can think of is that this is a process load and is therefore modeled identically. If the space conditioning is related to the equipment and not the occupants then perhaps it can be justified.