Forum discussion

Schools-2009 EAc5:Measurement and verification

Hot Water use

I'm working on a building that is part of a larger facility. The domestic hot water is produced at a central plant. Does anyone have experience with this and if so, did you monitor the energy use for the domestic water heating? If not, does anyone know if this is required? In looking into this, the focus appears to be on the HVAC systems.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/21/2012 - 21:55

In order to calibrate the model by each energy end use you must measure or be able to derive them all. Typically this means you collect some data (could be a spot measurement, short-term trend or permanent meter) on most systems. Since the energy use for DHW is not within the building it would seem to make sense to meter the incoming HW at least for a period of time. The focus of M&V is on determining energy savings, not just related to HVAC systems.

Wed, 08/22/2012 - 15:34

If it were only that simple, but with two connection points and hot water return, it actually means metering multiple water lines. But I do agree with your comment, it is about energy use, and there is energy there. Thanks,

Thu, 08/23/2012 - 12:52

This brings up an important issue. M&V needs to be planned during design. If you will need to sub-meter it is always better to plan for it in the design/layout of the system. This usually enables the sub-metering to be done as cheaply as possible. Not sure if it would have helped in your specific situation Jonathan but reading your post triggered that thought.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.