FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Hotel HVAC (electric) and DHW (gas) systems

Am I right to assume in the baseline building:

1 - The use of HVAC system 2 for all hotel spaces since it is considered a "Residential" building (according to table G3.1.1A of ASHRAE90.1-2007) ? Can we apply this system type to all zones (bedrooms, corridors, reception)?

To other zones (car parks, exercise center, restaurants), I am considering “nonresidential” building types.

2 - To decide which HVAC system to consider for all “nonresidential” area, I apply the criteria from table G3.1.1A to all “nonresidential” 2600 m2 with 5 floors and select system 6, correct?

3 - However, there are also spaces that fall under G 3.1.1 exception b (space peak thermal load that differ 31,2W/m2 or more than the average of the system). Does the calculation of the average thermal load regards only the nonresidential spaces? Or should I include in this calculations all the building’s area?

4 - Regarding the DHW system, there are 2 boilers  of 125 kW each (nominal nameplate power), serving 2 storage tanks of 3.000 liters each. The baseline DHW system that I'm choosing for the baseline is a Gas storage water heater, with more than 22,98 kW and, therefore, has 80% (Et), right?

 

Thank you in advance!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 02/22/2018 - 16:20

1. Yes assuming the proposed systems are electric heating. For the non-residential space first subtract the area of the residential spaces then enter Table G3.1.1A. 2. Yes only use the area of the non-residential spaces. 3. Any G3.1.1 exceptions should be relative to the majority of non-residential spaces. So yes only the non-residential spaces. 4. The DHW systems should use the same fuel type and be based on the same load unless claiming savings for a reduced hot water load.

Fri, 02/23/2018 - 09:48

Thanks Marcus!

Tue, 02/27/2018 - 10:16

Another issue came up! Regarding point 2): to determine the nonresidential HVAC system, must I include the "Car park" (unconditioned) building area? Thank you all in advance!

Tue, 02/27/2018 - 14:25

No. Just the conditioned space.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.