NC-2009 EAc3:Enhanced commissioning

Late Enhanced Comissioning

Does exist any time limit between the construction conclusion and the start of enhanced comissioning? i.e. To comply to this credit, can I contract the enhanced comissioning in a building that has been occupied for 11 months? Thank you!

5

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/16/2011 - 20:22

Are you considering enhanced commissioning for a NC project that is already complete? If the commissioning would be for systems that have already been constructed, the credit is not achievable. The commissioning design review of 50% CDs has to be completed by the party providing enhanced commissioning at that point in the schedule - so there is time for comments and changes to be incorporated into the final construction documents. If you're considering enhanced commissioning for a tenant improvement pursuing LEED CI in a building that is already built, well, that's a different story....

Tue, 04/26/2011 - 12:42

Agreed. Enhanced Cx should (must) be engaged during the design phase of the project (hopefully during schematic design). Commissioning of a completed building does not comply with the intent of the credit.