We have a LEED CS project where some ventilation systems are included in the tenant's scope of work, so I am working the owner to incorporate ASHRAE 62.1 compliance language into the lease agreement. Does anyone have an example of this that they would be willing to share with me?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/09/2015 - 16:34

The language for this can be really simplified to include that the future tenant will comply with the min. ventilation rates based on the reference standard; it wouldn't hurt to include TABLE 6-1 only for applicable spaces on your project. A clause that the EOR for the Tenant Finish out is responsible for the calculations to show compliance should also be included. Notes in CS drawings/floor plans stating "This area shall comply with the requirements of ASHRAE 62.1-2007. Please reference design guidelines or leasing agreement for more details" is also helpful.