FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

LEED CS 2009 Existing Equipment

could you clarify something for me: Existing HVAC equipment: 1. If it's not touched it may be used identically in the baseline and proposed case. 2. If it is changed, the baseline HVAC becomes the the ASHRAE 90.1 2007 min requirements table xx. 3. What about if it is modified? For example, an air handler is given a new ECM fan motor or equipped with a VFD. Does the baseline now require to use the fan power calc in the model? 4. Similar to above: What if the existing boiler is to remain but is now equipped with a new control system to provide HW reset and OA reset? Does the baseline require 90.1 App G to be modeled even the though the efficiency of the boiler in the proposed is worse? Any input you have would be greatly appreciated!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 02/15/2017 - 08:17

You have to model the baseline HVAC system according to G3.1.1, which reference Table G3.1.1A also for existing buildings. I.e., it doesn't matter if a HVAC system exists before the project.

Wed, 02/15/2017 - 14:36

In your email to me you had indicated that you noticed a shift in the responses on this subject. A few years ago GBCI reviewers were requiring the Baseline HVAC to always be according to Appendix G. That changed about 2012, which is why you may have noticed a shift in advice. 1. Existing HVAC is modeled identically.See Page G-21 in the 90.1-2007 User's Manual. 2. Correct. 3. This is a bit grey. What I would do is model the components that remain as existing identically and model the components that change according to Appendix G. 4. I would do the same as above here. Model the existing boiler efficiency identically since that did not change but model the controls as if they were new.

Wed, 02/15/2017 - 14:51

R2M - Your reply is in conflict with what is stated in the 90.1 2007 User's Manual. The manual states "unchanged components are modeled at their existing levels of energy performance" under section G3.1. Furthermore, there is an exception if an HVAC system exists: "...the proposed building and baseline building models are the same and are based on the existing HVAC system" under section HVAC systems of the User's Manual. What is LEED's stance on the statements above? Can you please help to clarify?

Wed, 02/15/2017 - 15:14

I summarized the current stance of the LEED/GBCI reviewers above. We were probably typing at the same time perhaps.

Wed, 02/15/2017 - 16:01

I'm sorry, my interpretation was wrong (at least for the current situation). Regards

Tue, 05/09/2017 - 10:49

Is the principle "...the proposed building and baseline building models are the same and are based on the existing HVAC system" valid also for the renewable energy sources and for the ventilation air flow rates (i.e., is exception c. of G3.1.2.6 not valid?)? Cheers

Tue, 05/09/2017 - 13:09

I'm not sure that is a principle. For an existing renewable I would think you could still get credit for it. They align so well with the intent of LEED and are rare enough that they should count no matter what IMO. There is a difference between an energy consuming system and an energy producing system. 90.1 does really deal with energy producing systems so much. As for the ventilation it needs to be identical in both models for an existing system and it needs to comply with ASHRAE 62.1. My copy of 90.1 does not have an exception c for G3.1.2.6?

Tue, 05/09/2017 - 13:25

Sorry, my comment was relative to ASHRAE 90.1-2010. Shall I write the question in the forum relative to LEED v.4?

Tue, 05/09/2017 - 13:36

Yes please

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.