FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Lighting Requirements for Hotel in Core and Shell

Hi everyone,

We are currently working with a mixed-use building which has offices, commerce and a hotel.

Our inquiry is regarding the hotel's section lighting project. Following ASHRAE 90.1-2007 considerations for this building type, this type of section should consider HVAC and building envelope within 'Residential' systems and constructions categories. Therefore, should our hotel adopt residential considerations in order to register lighting energy savings? By this we mean, do we have to work with 'Energy Star MFHR Simulation Guidelines' and its section 'In-Unit Lighting' with the assistance of its calculator? Or should we just model the installed lighting capacity of the hotel's proposed project for lighting savings?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 09/09/2017 - 17:44

No, hotel rooms are covered in 90.1 in Table 9.6.1 at 1.1 watts/sf.

Mon, 03/12/2018 - 14:57

Thank you, Marcus!

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.