FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Maintenance Garage Baseline System

I'm hoping someone can help me determine the appropriate Baseline system for a Vehicle Maintenance Facility for a LEED v2009 project. The total project area is about 34,500 s.f. however 28,000 s.f. of the building is a Maintenance Garage that will be heated only with unit heaters when the office area is only 6,500 s.f. Based on Table G3.1.1A it appears the Baseline should be System 5 for the total project area but if applied to just the conditioned area it would be System 3 and the Garage would be served by System 9 Wamr Air Furnaces. What is the appropriate approach for this condition? Thank you very much for your help.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 10/02/2017 - 16:52

Hi Keith, According to the building areas I think your second approach would be better. The building is mainly heating only so you can use system 9 for the maintenance area and you can use an exception for the offices and use system 3. I hope that helps.

Tue, 10/03/2017 - 11:40

Thanks Saif! This does appear to be the logical approach.

Thu, 10/05/2017 - 14:55

Agreed