Hello All, I have two questions about compliance with the mandatory provision: 1) Only the main air conditioning system should be evaluated with the tables in chapter 6? or if I have 2 or 3 small offices with teams split wall, they also must meet? 2) According to section 10.4 must be met given engine efficiency for motor 60Hz, according investigate this table comes from NEMA MG 10-2001 Publication Standars and this in turn is emulated with IEC 60034-30 for 50Hz. Is this correct or do not care if Chile motors low efficiencies are even lower than the IE2? Thanks for the reply.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Add new comment
To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.