NC-v4 EQp1:Minimum indoor air quality performance

Minimum IAQ Performance calculator

Why does the Minimum IAQ Performance calculator excel spreadsheet have a formula to truncate the calculation of the Average outdoor air fraction (Xs) to only 2 digits by rounding down? In my particular case it is rounding 0.199 down to 0.19 and pushing the required outdoor air flow above what I would otherwise design to. This rounding down seems unnecessary. Is there a way to get USGBC to fix the spreadsheet or are there other spreadsheet's available?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 04/29/2024 - 06:45

Hi, Because if you round down, then the design provision still can meet the requirement (even have buffer). But if you round up, then the design provision doesn't meet requirement actually.   Here is the latest calculator related to minimum IAQ performance credits: https://www.usgbc.org/resources/minimum-indoor-air-quality-performance-calculator To ask USGBC specifically, you can contact USGBC through this website and explain your situation: https://www.usgbc.org/contactus Hope this help. Best regards – Afogreen Build Team

Wed, 01/14/2026 - 11:41

I’ve noticed this too! Sometimes these official spreadsheets truncate or round numbers in ways that can affect design calculations, like your example with 0.199 rounding down to 0.19. If you want more control over decimal places, I’d recommend trying a good rounding calculator — it makes testing different rounding options quick and easy. You can check it out here: http://rounding-calculator.net/

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.