NC-v4 EQc8:Quality views

Museum/Galleries Regularly Occupied Spaces

Hello, Our project building include mostly museum/galleries and lobbies. The project building is very close the sea and has amazing landscape. Because of it, the building is designed as people can see easly the landscape via vision glazing when they spend time in lobbies and lounges. We believe that they can spend more than one hour in there. Can we specify this lobbies as regularly occupied spaces? Thank you

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 08/28/2017 - 11:39

Lobbies would be considered regularly occupied space. You can always include spaces that are not listed in the regularly occupied space matrix if they truly are occupied. Its when a space is listed in the matrix is when you have to provide a pretty valid reason for its exclusion.