FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

n/a

I wonder if there is a standard to convert C-factor to U-factor or F-factor to U-factor. Is there a guideline to do so? Since not all energy program can let you input C, U, F as you desire. Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/17/2015 - 15:38

They measure related things differently so I am not aware of any way to convert one to another. 90.1 Appendix A contains some guidance for how to model some assemblies if the software does not directly take F or C Factors.

Wed, 03/18/2015 - 08:15

App. A is rather inflexable with other methods for calculating F-factor u-values and specifically states that you can't. For example, you can't use a 2/3d FEM program in this case. The engineering reference for energyplus describes how the program "reverse engineers" an equivalent construction with concrete and insulation from the user F & C factor inputs. You'll find the pdf with google. It's a big document so you'll search for C-Factor and F-factor to find the right section. Several factors play a role...depth of wall, perimeter of slab, etc. But that's not all. The appropriate boundry conditions have to be applied to the "exterior" side of the element also during simulation. I made a slightly more detailed post regarding F-factors some time ago.

Wed, 03/18/2015 - 14:24

USGBC allows the following if the software does not model F-factor, model the Baseline slab-on-grade floor as a six inch concrete slab over earth with a soil conductivity of 0.75 Btu/h-ft-°F in accordance with A6.1.

Wed, 03/18/2015 - 14:27

Thanks all. Those are great info

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.