FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Natural ventilation

We are working on an industrial building which has 3 hangars which are occupied during working hours and its partly open and 24 hours natural ventilated. How should we address this building related to EAp2, as I can’t use cooling or heating for proposed or baseline due to the permanent openings? The energy performance has to be achieved only for those systems that will be provided by the owner as the hvac in the other rooms and the lighting system, in this case? Thank you

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 01/29/2014 - 15:05

If the space is not conditioned in the proposed case then it does not require heating or cooling in the baseline case. The energy performance has to be achieved by comparing the proposed project as designed with the Appendix G baseline.

Wed, 01/29/2014 - 16:34

Yes, but then I will have not enough energy reduction to achieve the minimum required for Prerequisite 2 of minimum energy performance, as most part of the building is natural ventilated and will not have any hvac system installed. Is it possible to take credit on natural ventilation as efficient measure as I am reducing the use of air-conditioning? If so, should I do it trough the exception calculation method? Thank you for your answer!

Wed, 01/29/2014 - 16:46

Sounds like you need to figure out how to get additional savings from the systems being installed. You can claim savings for natural ventilation and it would be an exceptional calculation. See Appendix D of the Advanced Energy Modeling Guide for LEED. You will need to demonstrate that the natural ventilation will deliver similar comfort conditions to a mechanically cooled space and use software that can model natural ventilation (many cannot do so). Even if you can do all of that I certainly would be highly skeptical of such a claim for a space which is not even fully enclosed. You would also have to justify any attempt to condition a space open to the outdoors.

Thu, 01/30/2014 - 08:59

This is IMO one of the trickiest areas in the system, i.e. conditioned areas that are open to the outdoors. Probably, it is the intent of USGBC to change industry trends for the better, so such areas should in principle seriously disadvantage the project from attaining LEED certification. Possibly, you could argue that the conditioning system serving the non-enclosed area is per say excluded from the scope of the 90.1 standard and should therefore be considered process loads on the system. In your case, you're stuck again with the problem that when almost the whole project energy is process, then you have very little "pie" left to gain efficiency advantages against the baseline. And prooving a process baseline would be neigh impossible, so having a different process load compared to the baseline is also a no go. Your suggestion to try showing a net energy savings from "natural ventilation", is a valid path, but it is probably more likely to show an enery wasting than an energy saving (this is the very reason why it is steared away from in all but the most ideal climates). Even properly designed natural systems have a hard time meeting both comfort and energy saving criteria. If this is a new construction, you should talk to the architect about standard 90.1 and don't forget about the vestibule requirements. Perhaps, they can make it a properly enclosed area.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.