FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Natural ventilation – modeling in Baseline

Greetings,

The project that we are modeling has zones with natural ventilation LEED v2009).

As there is no such ventilation systems in the Baseline model (System 5), our idea is to proceed as follows:

  • Proposed model – natural ventilation airflow is entered as infiltration

  • Baseline model – two options:

    • The air flow also to be entered as infiltration

    • The airflow determined as infiltration in the Proposed to be entered as ventilation air in the Baseline

Any support on the issue is highly appreciated.

Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 02/20/2019 - 18:56

How is the infiltration level determined?

Thu, 02/21/2019 - 09:33

The infiltration is determined based on the number of people, heating mode, Ez = 0.8, 30% increased ventilation. The values are in L/s. Thanks.

Mon, 02/25/2019 - 17:34

The infiltration (i.e. natural ventilation) should be modeled identically in both.