Forum discussion

EBOM-2009 EAc2.1:Existing building commissioning - investigation and analysis

Occupant service capabilities

Hi, Reviewer comment asks us to provide "The effect on occupant service capabilities" of the capital measures identified during the level II audit. I want to know what is the definition of "occupant service capabilities"? Thank you.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 11/05/2013 - 02:39

Magda, I don't know—never heard that term before. Can you provide a more complete quote?I would ask GBCI to clarify the reviewer comment.

Wed, 01/22/2014 - 14:05

"occupant service capabilities" is language from the referenced standard. It is asking how the implemented measure affects the occupant's ability to control/adjust their setpoints/operating hours/etc. Many times the practical capital improvement meausures we identify has no effect on ocupant service capabilities; therefore we note in our report 'not applicable to this capital improvement measure".