FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Perimeter Zones Requirements for Warehouse

Hi All, I am working on a large warehouse project, which is an open space with the area of 10,000 square meter. This project is targeting at LEED 2009. As the space is quite big, I just wonder if there are any requirements on creating perimeter zones or not. If treating it as one zone, will it influence the energy results? Has anybody have any experience on this? Many thanks in advance! Alice

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 01/12/2017 - 09:46

The baseline must be modelled as per ASHRAE 90.1-2007 app. G. Therein it tells you how to divide the perimeter into virtual zones. You should do this for the proposed model as well as it is good practice (most of the time, there could be situations where it is not depending on the radiation infall from outdoors). As a good rule of thumb...whereever there is a thermostat, model the zone that thermostat is suposed to control. Again, check the standard...there are some good tips in there.

Thu, 01/12/2017 - 10:09

Hi Jean, Thanks for your reply. I read the Table G3.1.7. To my understanding, the HVAC zones have been designed. There are four fan coil heaters distributed in the warehouse. Each air hear has a thermostat. However, I still wonder if it is required to divide the space into four zones as all the internal loads, system etc is the same throughout the warehouse. Many thanks.

Thu, 01/12/2017 - 15:29

To be honest, this is a modelling issue. The thing is that a zone is considered "well mixed" in most programs and does not take into account temperature variation across the zone as would occure in real life. To make sure the thermostats and systems respond "semi-realistically" it is usually a good idea to seperate these as suggested. However, it is situational and geometry together with air movement, both thermally induced and mechanically induced are really what should influence your judgement calls. Does that make sense?

Thu, 01/12/2017 - 16:22

In a warehouse you would not typically see any perimeter zoning except maybe by the loading docks. All things being equal in each of the 4 areas you could probably combine them into one thermal block without much of an impact on energy use. Combining areas into fewer thermal blocks in my experience is typically done to simplify the model. As Jean suggests this is a judgement call on the part of the modeler. Like all judgement calls you should be able to defend the actions you take as thermodynamically similar enough to only minimally affect the energy use.

Fri, 01/13/2017 - 09:11

I agree and would point out that Marcus says "loading docks", but basically think of other "zones" that may experience other dissimilar thermal loading as well. For example near a fully glazed wall or near a hot machine. The type of thermostat may also be a consideration. I'm in Europe and just this minute there's a project where we use radiative ceiling elements for heating combined with operative temperature thermostates. Here I would think about hot or cold radiative surfaces as well which may influence the thermostat and drive the heating surface temperatures of the radiative panels. In that case adding additional "virtual" surface to split zones may even negatively effect the thermostat reading, so I need to be careful. At the same time, large spaces (especially high ones) could show some stratification. My software can handle this by using a "non-well mixed" room air model to capture some of these effects without splitting the zone. I've not started this job, but these would be some of the thoughts that would go through my mind to consider. These kind of impacts start really mattering if the systems are ramping up and down and negatively effect efficiencies which is especially prevelant in radiant systems. Air systems tend to "well mix" better and not suffer from these control symtoms as much.

Fri, 01/13/2017 - 15:02

Hi All, Thanks for your reply. This warehouse has very few windows. And I already created separate thermal block for loading bays. I just wonder if it is right to treat the whole open-plan warehouse as one zone and adding the flow rates from each air heater together in the ApacheHVAC. Yes I understand that stratification may occur in the large space. But just wonder if it is necessary to do separate thermal blocks in this case to be in compliance with LEED requirements. Many thanks!

Fri, 01/13/2017 - 15:37

For LEED Table G3.1-7 tells you what you have to do. The exception for combining blocks will need to apply in order to combine zones into a single block. If all of the exception criteria apply then you can combine them. Jean has been trying to let you know the thinking that needs to go behind the combining of multiple zones into a single block.

Fri, 01/13/2017 - 15:47

I would divide the large open space into core and perimeter zones at a minimum. Since the the spaces are open to one another, I would make the partitions to be 100% hole.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.