CI-2009 EAc2:Enhanced commissioning

Question regarding the OPR and BOD

We have a client that has the Owners Project Requirements (OPR) but no Basis of Design (BOD). Is it acceptable for the OPR to be used in place of the BOD?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 03/18/2013 - 19:38

Robert, The OPR comes from the client. The BoD is a response to the OPR and is the A/E team saying how they are going to meet the OPR. It is not acceptable to use the OPR in lieu of the BoD. Susan

Mon, 03/18/2013 - 19:48

I concur with Susan, you need to submit both the OPR and the BOD.