FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Selection baseline cooling system for industry process

I am trying to select the baseline cooling system of a food industry. The process cooling requires more than 60% of total energy demand with temperature level of -44°C and -33°C (freezing circuit NH3). According to ASHRAE90.I 2007 2.3c the provision of ASHRAE do not apply to this system. 1. Is this cooling system really not applicable for LEED NC? 2. If applicable, which cooling system (which COP) can I assume for the. baseline? 3. If not applicable, should I analyse only the energy demand of office areas?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/24/2013 - 14:42

1 - It is and is not applicable. It must be included in the model but it does not have to comply with the mandatory provisions of 90.1 for example. 2 - The baseline should be modeled identical to the proposed and the proposed should be modeled as designed/installed. This assumes you are not attempting to claim any energy savings related to this system. 3 - It is applicable in that it must be included in the models.