FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Supply temperature for the baseline building

I am doing an ASHRAE 90.1-2007 PRM analysis. We have a DOAS CV laboratory design that has a requirement between 10-20ACH in lab zones and a room set point of 20degC. The baseline system is System 5 – Packaged VAV with Reheat Section G3.1.2.8 states airflow rates shall be sized off supply-air-to-room-air difference of 11degC, or the required ventilation air/makeup air, whichever is greater. In our case the required ventilation rate is greater than the flow rate using an 11degC temperature difference (supplying at 9degC). Design outdoor air requirement =12,400l/s Supply flow rate at 11degC temperature difference = 7,500l/s My question is, for the baseline building do we still supply our outdoor 12,400l/s air at 9degC + 2.3degC supply reset (G3.1.2.12) from the AHU? Doing this leads to the baseline overcooling to 11.3degC (9+2.3) and then re-heating to 17-18degC to achieve the space set-point of 20degC. This creates an inefficient baseline and therefore a positive effect for the energy cost saving. The same problem seems to have been posted here, with the answer suggesting that this is acceptable to overcool and then reheat: http://energy-models.com/forum/discourse/general-discussion/vav-minimum-flow-setpoint-and-supply-air-temperature-reset-ashrae Any help would be much appreciated.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/09/2016 - 20:39

It appears as if G3.1.1 exception d applies, so the 50% reduction applies during unoccupied periods. The rest of what you included above sounds right.

Thu, 03/24/2016 - 11:56

Marcus, thanks for your response. This proposed Laboratory system uses 2 AHU’s per floor, one AHU will be conditioning a wing to 25-35% RH 20degC during all occupied hours, the 2nd will be conditioning a wing to a more standard 40-70%RH 20degC. The baseline is system type 5, with one per floor. To achieve the low 25% to 35% RH and 20degC the proposed system is using chemical desiccant dehumidification. To achieve 25%-35% RH and 20degC in the baseline the cooling coil off coil temperature of System type 5 would need to be 2degC (using a psychrometric chart). Firstly, is it acceptable to change the baseline System type 5 cooling coil off coil temperature to 2degC, and therefore no longer be supplying at the 11degC delta T required by G3.1.2.8 (it would now be 18degC delta T). Secondly, because there is only one system per floor in the baseline, this would then mean both wings would have to be conditioned at 25-35%RH (rather than only one wing) as the baseline has no re-humidification method for the wing with 40%-70% RH requirement. Does this then mean the low RH% wing needs to be modelled as System Type-3 but still with the 2degC cooling coil off coil temperature? Thanks for your help.

Thu, 03/24/2016 - 12:09

Marcus, thanks for your response. This proposed Laboratory system uses 2 AHU’s per floor, one AHU will be conditioning a wing to 25-35% RH 20degC during all occupied hours, the 2nd will be conditioning a wing to a more standard 40-70%RH 20degC. The baseline is system type 5, with one per floor. To achieve the low 25% to 35% RH and 20degC the proposed system is using chemical desiccant dehumidification. To achieve 25%-35% RH and 20degC in the baseline the cooling coil off coil temperature of System type 5 would need to be 2degC (using a psychrometric chart). Firstly, is it acceptable to change the baseline System type 5 cooling coil off coil temperature to 2degC, and therefore no longer be supplying at the 11degC delta T required by G3.1.2.8 (it would now be 18degC delta T). Secondly, because there is only one system per floor in the baseline, this would then mean both wings would have to be conditioned at 25-35%RH (rather than only one wing) as the baseline has no re-humidification method for the wing with 40%-70% RH requirement. Does this then mean the low RH% wing needs to be modelled as System Type-3 but still with the 2degC cooling coil off coil temperature? Thanks for your help.

Thu, 03/24/2016 - 14:13

Marcus, thanks for your response. This proposed Laboratory system uses 2 AHU’s per floor, one AHU will be conditioning a wing to 25-35% RH 20degC during all occupied hours, the 2nd will be conditioning a wing to a more standard 40-70%RH 20degC. The baseline is system type 5, with one per floor. To achieve the low 25% to 35% RH and 20degC the proposed system is using chemical desiccant dehumidification. To achieve 25%-35% RH and 20degC in the baseline the cooling coil off coil temperature of System type 5 would need to be 2degC (using a psychrometric chart). Firstly, is it acceptable to change the baseline System type 5 cooling coil off coil temperature to 2degC, and therefore no longer be supplying at the 11degC delta T required by G3.1.2.8 (it would now be 18degC delta T). Secondly, because there is only one system per floor in the baseline, this would then mean both wings would have to be conditioned at 25-35%RH (rather than only one wing) as the baseline has no re-humidification method for the wing with 40%-70% RH requirement. Does this then mean the low RH% wing needs to be modelled as System Type-3 but still with the 2degC cooling coil off coil temperature? Thanks for your help.

Fri, 03/25/2016 - 15:04

1. No you can't change that parameter. 2. Check the exceptions to G3.1.1 to see if any apply. If they do you must implement them in the baseline. The humidity setting must be identical in both models. Any humidification system is considered a process load and must be modeled identically.

Wed, 03/30/2016 - 10:03

Thanks Marcus. To clarify, from reading your second point dehumidification should also be modelled identically? Therefore the baseline will need to be modelled with a desiccant dehumidifier identical to the proposed rather than reducing the baseline cooling off-coil temperature. I don’t see any other method for achieving the low RH requirement.

Wed, 03/30/2016 - 14:59

Dehumidification beyond what is required for the comfort of people would be considered a process load and should also be modeled identically.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.